Using AI to Do an Engineer’s Work

Steven Turner, ConsultantColumns, Relay Column, Summer 2026 Columns

Recently, I challenged a proprietary AI platform to solve a simple protection problem: Use a CO-9 overcurrent relay to provide backup protection for a 150 MVA transformer; the high-side voltage is 230 kV. Plot the characteristic of the CO-9 versus the transformer damage curve. This was not an especially difficult problem to solve. I wanted to see if it would …

Using the KD-10 to Provide 78 Out-of-Step Tripping Protection for a Large Generator

Steven Turner, ConsultantColumns, Relay Column, Spring 2026 Columns

Typically, multi-function numerical generator protection relays are now used to provide out-of-step tripping (OST) for large unit-connected generators. However, some users prefer to maintain older existing infrastructure, such as electromechanical relays. 78 OST protection must meet PRC-026-2 Criterion A of Attachment B requirements as follows: PRC-026 Criterion A of Attachment B indicates that a 78 impedance-based out-of-step protection function should …

Sizing the Neutral Grounding Resistor for Subharmonic Voltage Injection

Steven Turner, ConsultantColumns, Relay Column, Winter 2025 Columns

Stator ground faults are one of the most common disturbances for high-impedance grounded generators. A resistor is connected across the secondary of a single-phase distribution transformer connected from the machine neutral to ground to insert the high-impedance ground. The purpose of the high-impedance ground (Figure 1) is to limit the magnitude of single line-to-ground fault current flowing in the stator …

Transformer Differential Logic to Prevent Unwanted Trips during CT Saturation for External Faults

Steven Turner, ConsultantColumns, Relay Column, Summer 2025 Columns

Modern numerical transformer protection relays have powerful logic to prevent unwanted tripping on phase differential during CT saturation for external faults. This article analyzes this logic for a typical application. To demonstrate these protection features, we will simulate the low-side fault current for an out-of-zone fault using the IEEE PSRC CT Saturation Calculator. Note that this type of exercise is …

Improvements to REF Protection for Low-Resistance Grounded Systems

Steven Turner, ConsultantColumns, Relay Column, Spring 2025 Columns

A restricted earth fault (REF) protection element provides sensitive detection of ground faults near the neutral of a transformer wye-connected winding. The sensitivity gains from the REF element are especially more valuable if the equipment is low-impedance grounded. Security of the REF element may be jeopardized by external faults, such as a phase-to-phase-to-ground or an evolving fault with CT saturation. …

Distance Protection Impedance Measurement Fundamentals: Phase-to-Phase and Phase-to-Ground Faults

Steven Turner, ConsultantColumns, Relay Column, Winter 2024 Columns

Distance protection measures loop impedances to determine the location of a fault on the protected line. There are six loops: A-B, B-C, C-A, A-G, B-G, and C-G. This article demonstrates how distance protection measures the apparent loop impedance for B-Phase-to-C-Phase and A-Phase-to-Ground faults. The loop impedances for phase-to-phase and phase-to-ground faults are not equivalent due to the presence of neutral …

Basics of Breaker Failure Protection

Steven Turner, ConsultantColumns, Fall 2024 Columns, Relay Column

Breaker failure protection provides backup protection in case the local circuit breaker fails to clear a system fault. If a breaker fails to trip, adjacent breakers must be tripped to isolate the fault from the sources feeding it.  Figure 1 illustrates a fault on the transmission line served by Breaker 3 and Breaker 4. If Breaker 3 fails to open, Breaker 2, Breaker 5, and …

Optimizing 50/27 Inadvertent Energization Protection

Steve Turner, Arizona Public Service CompanyColumns, Relay Column, Summer 2024 Columns

The 50/27 inadvertent energization protection function (Figure 1) is an overcurrent function supervised by generator terminal bus voltage derived from system-side voltage transformers (VTs). Inadvertent or accidental energizing of off-line generators has occurred frequently enough to warrant using dedicated protection logic to detect this condition. Operating errors, breaker flashovers, control circuit malfunctions, or a combination of these causes have resulted …

OOPS Protection Scheme Logic

Steve Turner, Arizona Public Service CompanyColumns, Relay Column, Spring 2024 Columns

An out-of-phase synchronization (OOPS) event results in a torque transient on the generator and prime mover. It exposes the generator, generator step-up (GSU) transformer, and system elements to a current transient that puts mechanical and thermal stresses on windings and other conductors.  These transients can be significant and result in through-current magnitude equivalent to a three-phase fault located at the …

Effect of CT Saturation on Transformer Differential Protection

Steve Turner, Arizona Public Service CompanyColumns, Relay Column, Winter 2023 Columns

This article demonstrates how current transformer (CT) saturation can adversely affect transformer differential protection and how to easily mitigate its effects via inbuilt relay functions. We provide calculations and simulation for a three-phase fault on the low side of the transformer just external to the CTs. APPLICATION The application is for a three-phase delta-wye connected transformer serving station at a …