This article demonstrates how current transformer (CT) saturation can adversely affect transformer differential protection and how to easily mitigate its effects via inbuilt relay functions. We provide calculations and simulation for a three-phase fault on the low side of the transformer just external to the CTs.
APPLICATION
The application is for a three-phase delta-wye connected transformer serving station at a power plant.
Transformer Name Plate Data
Size = 1.5 MVA
XT = 6.77% on transformer base
kVwdg1 = 12.47 kV
kVwdg2 = 480 V
CTR1 = 500:5
CTR2 = 4000:5
CT2 Data from Manufacturer Data Sheets
RCT = 1.861 ohms (0.002326 ohms per turn)
VS = 190 V (saturation voltage at excitation current equal to 10 amps)
System Data
X/R = 6.777
Fault Current Calculations
Calculate the low-side fault current as shown in Figure 1 (ignoring system impedance for worst-case scenario).
SIMULATION
Obtain the corresponding secondary current using a CT saturation simulation (Figure 2).
OBSERVATIONS
The secondary current is most distorted during the first cycle of the fault. To help mitigate unwanted tripping during the external fault condition, enable harmonic restraint (Figure 3) for the transformer differential protection.
Harmonic blocking is not enabled since it can delay tripping during internal faults. A note from the relay vendor specifications for this particular relay states that the transformer differential protection operates slower when harmonically restrained, which can also help ride through the period of saturation.
CT saturation can occur during faults external to transformer differential protection. Using harmonic restraint can help mitigate unwanted tripping during such events. Test the transformer protection relay to ensure the harmonic restraint works properly.